Air conditioner size is measured in “tons.” However, the tonnage of an HVAC unit is not actually based on its weight. A “ton” is simply a measure of an air conditioner’s ability to cool your home. One ton is the ability of your air conditioning system to cool 12,000 BTUs (BTU stands for British Thermal Unit) in an hour. Likewise, a “2-ton” central air conditioner is able to cool 24,000 BTUs per hour.

My mom just received service from this company. She paid $609 to have her frion replaced. After two uses the AC stops working. A young rep comes out to the house again and notifies her that her entire AC unit and furnace need to be replace for just shy of ten grand, though when her frion was refilled she was told that her system should last another five years. When they came back to tell her how her entire system needed to be replaced, they were generous enough to offer her a $300 credit on the nearly $10,000 estimate of replacing the entire system that was working fine until they touched it. My best assumption would be that there is a mishap with the system is due to their negligence. Id suggest using another company other than these scam artists.
Rheem's RRNL features a scroll compressor with fewer moving parts and less noise than traditional reciprocating compressors. A louvered compressor compartment protects the compressor from the elements and from debris that can shorten the life of the compressor. The Classic series continues to be one of their best sellers, with the addition of the Comfort Alert diagnostics module integrated to assist technicians in the event your system needs repair. 2-5 tons, 13 SEER, 80% AFUE.
The number of years an HVAC system lasts depend on the type and brand of components that make up your system. The lifespan of an air conditioner averages between 15 and 20 years. The life expectancy of a tankless water heater is approximately 20 years, while a storage water heater is closer to 10-15 years. Ducts may need replacing within 10-15 years. Your equipment will have a longer life if you have regular tuneups and maintenance to keep everything in good working order. If you’re having repair problems and your HVAC system is over 10 years old, it’s a good time to consider the costs and benefits of repairing vs. replacing. Energystar.gov provides the following tips to help you decide whether to repair or replace:

If you believe that the AC's not working or you're getting little or no cold air, check these three things first. Make sure all the registers in the house are wide open. Then be sure the furnace filter is clean. Then go outside and clean off the condenser coils (Photo 2). If several registers were closed or the filter was clogged, the reduced airflow could have caused the evaporator coil to ice up and stop cooling your home. If you've changed the filter and opened all the registers and you're still not getting airflow at the registers, deice the A-coil. Move the thermostat mode switch from “Cooling” to “Off” and move the fan switch from “Auto” to “On.” Let the blower run for at least 30 minutes or until there's good airflow at the registers. Then turn the AC back on to test it. If it works for the next 12 hours, you've solved the problem.


An air conditioning system's SEER is especially important if you live in a climate that changes temperature dramatically. The SEER is determined by the cooling output during the winter divided by its electric input during the winter. The higher the rating, the more efficient it will be. In January of 2006, the U.S. put standards in place for cooling units which are still in effect today. They must have a minimum SEER of 13. So, if you live in a home with a system installed before the new standards went into effect, consider having it replaced. SEER 13 units increase home efficiency by 30 percent.


An air conditioning system's SEER is especially important if you live in a climate that changes temperature dramatically. The SEER is determined by the cooling output during the winter divided by its electric input during the winter. The higher the rating, the more efficient it will be. In January of 2006, the U.S. put standards in place for cooling units which are still in effect today. They must have a minimum SEER of 13. So, if you live in a home with a system installed before the new standards went into effect, consider having it replaced. SEER 13 units increase home efficiency by 30 percent.

Deciding if central air is worth the cost depends on your needs and local housing market. If you live in a hotter climate, it can definitely be worth the price. Not only can it keep your home at a comfortable temperature, but air conditioning can even save lives during extreme heat waves. But in a milder zone without severe temperatures, window units, fans or the breeze from an open window could be adequate.
Natural ventilation is the ventilation of a building with outside air without using fans or other mechanical systems. It can be via operable windows, louvers, or trickle vents when spaces are small and the architecture permits. In more complex schemes, warm air is allowed to rise and flow out high building openings to the outside (stack effect), causing cool outside air to be drawn into low building openings. Natural ventilation schemes can use very little energy, but care must be taken to ensure comfort. In warm or humid climates, maintaining thermal comfort solely via natural ventilation might not be possible. Air conditioning systems are used, either as backups or supplements. Air-side economizers also use outside air to condition spaces, but do so using fans, ducts, dampers, and control systems to introduce and distribute cool outdoor air when appropriate.
The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.
An energy recovery ventilator: This component helps improve the air inside your home by swapping it out with fresh air from the outside. During the winter months when houses are closed up to keep out the cold, the air inside becomes a handy way for colds and flu to infect an entire family. By circulating outside air inside, the health of your family will have a better chance.
An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]
Heating, ventilation, and air conditioning (HVAC[1]) is the technology of indoor and vehicular environmental comfort. Its goal is to provide thermal comfort and acceptable indoor air quality. HVAC system design is a subdiscipline of mechanical engineering, based on the principles of thermodynamics, fluid mechanics and heat transfer. "Refrigeration" is sometimes added to the field's abbreviation, as HVAC&R or HVACR or "ventilation" is dropped, as in HACR (as in the designation of HACR-rated circuit breakers).

My heat pump/hvac system is not blowing cold air anymore, got checked out was told compressor broken. was told it cost  almost the same to repair/replace they recommend whole system. It's the same company that installed it 18 years ago, telling me that system is old and it will cost $9-10k for new system, because furnace has to be replaced with new hvac. what to do, need answers thanks????


Furnace Circuit Board -- The furnace circuit board controls a variety of functions. It not only handles the regular operation of the furnace, it also monitors the furnace's various safety circuits. Over time, vibrations from the furnace can weaken solder point and cause them to separate. Dirt and debris can cause short-circuits that damage the board. Failure of the circuit board can cause a variety of effects ranging from the fan not turning on to the complete shutdown of the furnace.
Installing a split system may involve making modifications to the house itself for the necessary lines to be run. The heat exchangers are also more prone to picking up debris and must be cleaned on a regular basis. While they come with protective screens over the fan, care must still be taken to ensure that nothing gets in, especially in a home with children.
Before we get to HVAC installation prices, we will first need to briefly discuss some terms, definitions, and factors that will affect how an honest HVAC installation company determines their prices. Notice that I said honest. Unfortunately, there are dishonest people out there. There always have been, there always will be, and there is a good chance that you had an experience with such a contractor, which is what drove you to read this article. I can’t teach you how to tell if someone is honest, but I can give you the knowledge to help you decide. Take a look at How to Choose an HVAC Contractor for tips on what to look for.
Many central air conditioning systems use the furnace blower to distribute cool air through the home. If you do not have a central heating system installed, it is cost-effective to install a heating and air conditioning system at the same time. If you already have central heat, you can use the existing fans and duct system for the central air system.

Whether or not central air adds value to your home depends on your location. You probably won't recoup the entire cost for the installation, as it is an expensive project that isn't as flashy as something like a new deck. But this invisible upgrade can help you sell your home if you live in a hot climate. And many buyers are willing to pay a bit more for a working AC.
If you believe that the AC's not working or you're getting little or no cold air, check these three things first. Make sure all the registers in the house are wide open. Then be sure the furnace filter is clean. Then go outside and clean off the condenser coils (Photo 2). If several registers were closed or the filter was clogged, the reduced airflow could have caused the evaporator coil to ice up and stop cooling your home. If you've changed the filter and opened all the registers and you're still not getting airflow at the registers, deice the A-coil. Move the thermostat mode switch from “Cooling” to “Off” and move the fan switch from “Auto” to “On.” Let the blower run for at least 30 minutes or until there's good airflow at the registers. Then turn the AC back on to test it. If it works for the next 12 hours, you've solved the problem.
The HVAC industry is a worldwide enterprise, with roles including operation and maintenance, system design and construction, equipment manufacturing and sales, and in education and research. The HVAC industry was historically regulated by the manufacturers of HVAC equipment, but regulating and standards organizations such as HARDI, ASHRAE, SMACNA, ACCA, Uniform Mechanical Code, International Mechanical Code, and AMCA have been established to support the industry and encourage high standards and achievement.
Indoor Coil -- The indoor coil is a heat transfer device. It absorbs the heat from the inside of the house and passes it on to the refrigerant and is pumped outside. Dust that builds up on the coil can hamper its ability to absorb heat. High heat transference coils use very thin metal. Airborne chemicals can cause corrosion which leads to leaks. The constant vibration of the compressor can also cause solder joints to weaken and leak. An indoor coil may operate for weeks with a tiny leak, and you may not notice the loss in performance right away. As soon as a leak is made known, it should be replaced or repaired immediately.
HRV/ERV Ventilators: These whole-house ventilators exchange air. They are ideal for homes with what is called a “tight envelope,” homes where house wrap has been applied and airgaps in the attic, around windows, doors and outlets have been sealed. Air in these homes becomes stale and polluted, so exchanging the air is important to IAQ. Heat recovery ventilators (HRV) are designed for cold climates. Energy recovery ventilators (ERV) are best for warm climates.  Your cost for an installed HRV or ERV will range from about $2,000 to more than $5,000 based on its capacity and features.
Appliance Repair in Fayetteville Appliance Repair Santa Barbara Lansing, MI Appliance Repair Augusta, GA Appliance Repair Appliance Store Raleigh York Appliance Repair Appliance Repair Austin Appliance Repair Topeka Appliance Repair Louisville Appliance Repair Salem, NH Paducah, KY Appliance Repair Evansville Appliance Repair Toms River, NJ Appliance Repair Appliance Repair in Easton, PA
×