All modern air conditioning systems, even small window package units, are equipped with internal air filters. These are generally of a lightweight gauze-like material, and must be replaced or washed as conditions warrant. For example, a building in a high dust environment, or a home with furry pets, will need to have the filters changed more often than buildings without these dirt loads. Failure to replace these filters as needed will contribute to a lower heat exchange rate, resulting in wasted energy, shortened equipment life, and higher energy bills; low air flow can result in iced-over evaporator coils, which can completely stop air flow. Additionally, very dirty or plugged filters can cause overheating during a heating cycle, and can result in damage to the system or even fire.
If you are using existing ducting, it will have to be inspected. Proper ducting loses around 2% to 5% of your energy. Old, leaking ducts can lose 50% or more. A contractor will need to have the ducts inspected and replace any parts ahead of time. If you are changing the size of your HVAC system because of significant changes to your home, you might need to replace the ductwork regardless.

Installing a split system may involve making modifications to the house itself for the necessary lines to be run. The heat exchangers are also more prone to picking up debris and must be cleaned on a regular basis. While they come with protective screens over the fan, care must still be taken to ensure that nothing gets in, especially in a home with children.

These are the prices for a proper installation from a professional – as a word to the wise, HVAC systems require fine tuning and the custom fabrication of parts during installation to work properly, otherwise they will likely fail prematurely. But there are plenty of people who will do it for cheaper than this, using substandard, used, or stolen equipment (stolen from construction sites and new housing developments). Or, they are using unskilled laborers with no experience, etc. But HVAC is not a “we’ll figure it out trade;” there is a right way and a wrong way to do things. There are just too many predatory companies out there, so be careful. I’d highly recommend not skimping on your HVAC contractor. If you go cheap, you will typically pay more in the long run...and in California, that will be a lot!
Roof-mounted systems have the heating and cooling systems in one cabinet. Sometimes called "gas packs" (if the heater uses natural gas), they typically cost less than a comparable split system. In dry regions, most homes originally had "swamp-coolers" installed. When replacing them with HVAC systems, it's often cheaper to use existing mounts and ducting.
Installation: The old furnace is disconnected from the ductwork plenum, exhaust flue, gas and electrical hookups. In most cases, a new plenum must be made onsite or ordered from a local sheet metal fabricator. A new vent might be required too. The furnace is set and reconnected. Adjustments to the blower fan speed and burner are made to optimize furnace performance for your home and climate.
Pro HVAC company Southern Comfort Mechanical says on its blog, “If there’s mold growth inside the handler due to excess moisture, algae in the condenser drain line or a dirty evaporator coil, it can negatively impact your AC unit’s efficiency. The filters inside may also build up excess dirt and become clogged, which will also make your AC [or heat pump] waste energy trying to sustain the cool climate inside your home.” These issues are easy to solve. They don’t require replacing the air handler.
In variable climates, the system may include a reversing valve that switches from heating in winter to cooling in summer. By reversing the flow of refrigerant, the heat pump refrigeration cycle is changed from cooling to heating or vice versa. This allows a facility to be heated and cooled by a single piece of equipment by the same means, and with the same hardware.
Installation: Replacement is quite easy, especially when an old refrigerant line set can be used. If the set is worn, it’s much better to pay the extra $400-$600 to replace it rather than risking it leaking later. When your AC loses refrigerant, you lose your cool air and the compressor is at risk of failing. A new installation means installing a coil in your furnace or air handler, running the line set between it and the coil in the condensing unit and adding refrigerant, if needed. Most ACs come pre-charged for 20-30 feet of line. If the line set is longer, a small amount of refrigerant is added.

Because an air conditioner moves heat between the indoor coil and the outdoor coil, both must be kept clean. This means that, in addition to replacing the air filter at the evaporator coil, it is also necessary to regularly clean the condenser coil. Failure to keep the condenser clean will eventually result in harm to the compressor, because the condenser coil is responsible for discharging both the indoor heat (as picked up by the evaporator) and the heat generated by the electric motor driving the compressor.
The sky is the limit. I am a big fan of adding zoning systems, but realize that this will typically add $2,300 to $3,500 (or more) to the price. “Why a price range, isn’t it just a part?” No, the part then has to be installed, and the customized ductwork required will vary based on the difficulty of the job and layout of your attic. It is very labor intensive, and most people don’t do it right. It should also include a bypass damper and ductwork! Simply put, the more you add, the more it will affect your HVAC installation cost.
Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]

The HVAC industry is a worldwide enterprise, with roles including operation and maintenance, system design and construction, equipment manufacturing and sales, and in education and research. The HVAC industry was historically regulated by the manufacturers of HVAC equipment, but regulating and standards organizations such as HARDI, ASHRAE, SMACNA, ACCA, Uniform Mechanical Code, International Mechanical Code, and AMCA have been established to support the industry and encourage high standards and achievement.
If the condenser coils are clogged, the compressor can overheat and shut down. You'll experience intermittent periods of minimal cooling, followed by no cooling. Even if you're “sure” the condenser coils are clean, clean them again. Turn off the power. Flip the air conditioning service and furnace circuit breakers in your main electrical panel to the “Off” position. Next, turn off the power switch right at the furnace or air handler. Then yank the disconnect block (Photo 1) and clean the condenser coils (Photo 2). If the air conditioning service still doesn't work properly after you've cleaned the condenser coils, installed a new filter and opened all the supply vents, proceed with the following repairs. Your AC won't work fully unless you do this.

Some systems include an "economizer mode", which is sometimes called a "free-cooling mode". When economizing, the control system will open (fully or partially) the outside air damper and close (fully or partially) the return air damper. This will cause fresh, outside air to be supplied to the system. When the outside air is cooler than the demanded cool air, this will allow the demand to be met without using the mechanical supply of cooling (typically chilled water or a direct expansion "DX" unit), thus saving energy. The control system can compare the temperature of the outside air vs. return air, or it can compare the enthalpy of the air, as is frequently done in climates where humidity is more of an issue. In both cases, the outside air must be less energetic than the return air for the system to enter the economizer mode.


So, the total price to a contractor for this project is $7,195.77 (Carrier is expensive), which we’ll use to calculate a fair HVAC installation cost. As I said, we typically use 40% in the industry to cover our own personal profit, as well as our insurance and other expenses. Let’s take a look at page three of a Final Report from our own online HVAC calculator, the HVAC Design & Consultation Program.
It's always changing: Some newer thermostats take advantage of wireless technology. You can adjust your thermostat remotely so that if you leave and forget to adjust it, or if you are going to be home later than you thought, you can adjust it via your smartphone. Some can even give you reports on how efficient your system is performing based on usage. These are very efficient models, but they are also very expensive with some costing over $250.00.
In modern buildings, the design, installation, and control systems of these functions are integrated into one or more HVAC systems. For very small buildings, contractors normally estimate the capacity and type of system needed and then design the system, selecting the appropriate refrigerant and various components needed. For larger buildings, building service designers, mechanical engineers, or building services engineers analyze, design, and specify the HVAC systems. Specialty mechanical contractors then fabricate and commission the systems. Building permits and code-compliance inspections of the installations are normally required for all sizes of building.
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.

Appliance Maintenance Book Snow Blower Maintenance Appointment Schedule Appointment for HVAC Maintenance Carpet Cleaning Services Air Duct Cleaning Services Handyman Service Riding Mower Maintenance Sears Warranty and Satisfaction Guarantee Heating and Cooling Home Renovation Tulsa Window Replacement Home Kitchen Design Roof Installation & Replacement Service Home Improvement Cabinet Refacing & Replacement Home Improvement
Our unit is 16 years old and we've had it checked out recently since it seems to be running excessively. Over all the tech says it is putting out well; it's the correct size, we have no shade and we've been having extreme heat with high humidity. The info you provided is very helpful and will help us make an informed decision when the time comes. Thank you so much.
The University of Virginia - 2005 / The Wharton School of Finance - 2016 / U.S. Naval Aviator 2005-2015. At All Systems Mechanical air conditioning and heating, we believe that the experience our clients have is every bit as important as the products they receive. Simply put, our results speak for themselves, and we'd be happy to help. If you're in the market for a new AC or furnace, make sure that you get a fair price! Try our online calculator; click the tab on the top of this page for more information.
AC units and thermostats have built-in delay features when they're shut down and then repowered. The delay can be as long as 10 minutes. And, if you've subscribed to an energy-saving device from your local power utility, the unit can take even longer to reset. If you've installed the parts shown and reinstalled the disconnect block, repowered the circuit breaker, turned on the switch at the furnace, moved the thermostat to AC mode and lowered the temperature below the indoor temperature, and the unit doesn't fire up after 30 minutes, it's time to call a pro.
R-22 Freon is being phased out & isn't readily available. So the service company may only purchase as needed and the lack of availability would make their cost high. But, as long as they can get it, whatever the cost, unfortunately, is less expensive than replacing the A/C. Which will be the case eventually since it's no longer manufactured or sooner as in my case with a not so old a/c that sprang a leak, that would have been just a repair, but since it uses R-22 the whole unit has to be upgraded(replaced).  
After one company just took a cursory glance at our A/C and found nothing wrong, I called HVAC. I called them mostly based on Michael W's post on 8/10/14 where he told us the owner, Alberto, took his feedback and took it SERIOUSLY. That speaks VOLUMES to anyone who has been around long enough to know the characteristics of the serious players are and those who are the wannabes.

7 To test it, turn the thermostat to OFF, reset the power at the disconnect next to the compressor and the main panel. Set the thermostat to a temperature below the room temperature, and then switch it ON. To avoid straining an air conditioner’s compressor, wait at least five minutes between turning it off at the thermostat and turning it back on. You should hear the outdoor compressor run and see the fan turning inside the top. If the fan isn’t turning, look for an overload button or switch to reset (not all types have this).

×