Heaters exist for various types of fuel, including solid fuels, liquids, and gases. Another type of heat source is electricity, normally heating ribbons composed of high resistance wire (see Nichrome). This principle is also used for baseboard heaters and portable heaters. Electrical heaters are often used as backup or supplemental heat for heat pump systems.

As for the price I think my review was fair in stating what value we got for what I deemed to be a slightly higher price than others might charge.  I did not take any stars off for the price, and still am not, but I am taking another star off because of Alberto's comments, which are deceptive and not the same thing he told me in person.  Alberto, I suggest you stick with the high road in the future.
Fast forward 1 year and 1 week and the circuit board that HVAC Service had installed has failed again. They came out and said that it failed from water condensation dripping onto it, so we needed to replace it and reroute the pipes to prevent future water damage.  That would cost double what I paid last year.  Why didn't they fix the problem last year at the initial repair instead of putting in a circuit board that was bound to fail again?!? They were strongly recommending that the furnace be completely replace for a huge fee to avoid the same thing happening again.  I paid $59 for them to tell me they didn't fix it right last year. This didn't feel right, so I sought a second opinion.

The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.


An example of a geothermal heat pump that uses a body of water as the heat sink, is the system used by the Trump International Hotel and Tower in Chicago, Illinois. This building is situated on the Chicago River, and uses cold river water by pumping it into a recirculating cooling system, where heat exchangers transfer heat from the building into the water, and then the now-warmed water is pumped back into the Chicago River.[24]
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.
Be careful with HVAC change-outs.  Change-outs are only about 15-20% of the HVAC installation industry. Decrease HVAC installation cost by investing in new ductwork now if needed. Your ducts wear out too, and make sure that your ducts are in fantastic shape if you do this. Many contractors push this because it’s easy and cheap for them, with good pay-off. Do your research and replace them if you need to in order to avoid doing it later, as well as avoid potential health hazards from using old, broken ductwork.
Installing a split system may involve making modifications to the house itself for the necessary lines to be run. The heat exchangers are also more prone to picking up debris and must be cleaned on a regular basis. While they come with protective screens over the fan, care must still be taken to ensure that nothing gets in, especially in a home with children.
Just had my HVAC System restored and working again on a Sunday and before the 104 weather tomorrow!!!! Called Big Mountain Heating and Air and spoke to very helpful woman named Martina. She connected me to a Technician named Josh. He was at my home within a few minutes and tackled my Honey Well system's issues. He is both skilled, personable and better yet, he got my system up and going and safe. He installed a surge suppressor on the system to prevent power surges that can kick off any system, when the electric company has to reduce power, etc.  I will be using Big Mountain in the future. Truly grateful for such good service and people. Thank you!  I recommend this firm to everyone!

Your contractor will do a load calculation to determine the proper central air conditioning unit for your home. This calculation accounts for the climate, size, shape and orientation of your home, as well as its square footage. A professional will also look at the insulation, windows, walls, floors and other materials that compose your home. He/she will then examine any leaks, seals and existing ducts or vents.
Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.
You can install the greatest HVAC system ever built, but if your house is not insulated well, it's only going to end up costing you more money. Older homes may have fiberglass insulation that has broken down due to pests, moisture, or improper installation. Spray foam insulation can be damaged by careless repair or modification work or can be improperly installed. If your insulation in compromised, your attempts to save money and be comfortable will be in vain.
But Tim, doesn’t this mean that a less-than-honest air conditioning company can just charge what he wants and say that it’s a difficult job? No. You see, dishonest contractors, typically, aren’t the brightest people (I figure if you’re still reading this, you’re warming up to me so I’m taking off the training-wheels). They aren’t smart enough to take difficulty into account, and will probably get confused if you ask them about it. They will tell you things like, “that’s how much the unit costs,” or “California has a new law that magically adds $5,000 to the price.”  Trust me, follow your gut, and you’ll be able to tell who the honest contractors are...or just use one of our ASM-approved contractors.
Clean the condenser fan blades before the start of the cooling season. Brush any dust or debris off gently and then uncover the condenser coils, gently cleaning the dirty side. Then wrap the motor and other electrical components in plastic bags and gently spray from the inside with a hose. Now check the base pan under the unit and clear it out of any debris that has gathered.
Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).
Hi John, Thanks for reaching out, we would be happy to help you connect with a pro for your project. You can submit a request to our pros here: www.homeadvisor.com, browse a list of pros that serve your area here: http://www.homeadvisor.com/c.html, or send your info to emailus@homeadvisor.com and a project advisor will reach out to assist you. –HASupport
If you believe that the AC's not working or you're getting little or no cold air, check these three things first. Make sure all the registers in the house are wide open. Then be sure the furnace filter is clean. Then go outside and clean off the condenser coils (Photo 2). If several registers were closed or the filter was clogged, the reduced airflow could have caused the evaporator coil to ice up and stop cooling your home. If you've changed the filter and opened all the registers and you're still not getting airflow at the registers, deice the A-coil. Move the thermostat mode switch from “Cooling” to “Off” and move the fan switch from “Auto” to “On.” Let the blower run for at least 30 minutes or until there's good airflow at the registers. Then turn the AC back on to test it. If it works for the next 12 hours, you've solved the problem.
Replacing a capacitor is easy. Just take a photo of the wires before disconnecting anything (you may need a reference later on). Then discharge the stored energy in the old capacitor (Photo 4). Use needle-nose pliers to pluck one wire at a time from the old capacitor and snap it onto the corresponding tab of the new capacitor. The female crimp connectors should snap tightly onto the capacitor tabs. Wiggle each connector to see if it's tight. If it's not, remove the connector and bend the rounded edges of it so it makes a tighter fit on the tab. When you've swapped all the wires, secure the new capacitor (Photo 5).
An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]
An air conditioning system, or a standalone air conditioner, provides cooling and humidity control for all or part of a building. Air conditioned buildings often have sealed windows, because open windows would work against the system intended to maintain constant indoor air conditions. Outside, fresh air is generally drawn into the system by a vent into the indoor heat exchanger section, creating positive air pressure. The percentage of return air made up of fresh air can usually be manipulated by adjusting the opening of this vent. Typical fresh air intake is about 10%.

Within the construction sector, it is the job of the building services engineer to design and oversee the installation and maintenance of the essential services such as gas, electricity, water, heating and lighting, as well as many others. These all help to make buildings comfortable and healthy places to live and work in. Building Services is part of a sector that has over 51,000 businesses and employs represents 2%-3% of the GDP.

An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.
Ventilation is the process of changing or replacing air in any space to control temperature or remove any combination of moisture, odors, smoke, heat, dust, airborne bacteria, or carbon dioxide, and to replenish oxygen. Ventilation includes both the exchange of air with the outside as well as circulation of air within the building. It is one of the most important factors for maintaining acceptable indoor air quality in buildings. Methods for ventilating a building may be divided into mechanical/forced and natural types.[16]
You've probably noticed many appliances boasting an Energy Star Certification. What this means is that manufacturer voluntarily built the product to help reduce greenhouse gases and meet non-regulatory guidelines offered by the Environmental Protection Agency. To earn an Energy Star rating, a product or system must be tested by a third party that has been recognized by the EPA for meeting their testing qualifications.
In the case of heated water or steam, piping is used to transport the heat to the rooms. Most modern hot water boiler heating systems have a circulator, which is a pump, to move hot water through the distribution system (as opposed to older gravity-fed systems). The heat can be transferred to the surrounding air using radiators, hot water coils (hydro-air), or other heat exchangers. The radiators may be mounted on walls or installed within the floor to produce floor heat.
Outdoor Fan Motor -- The outdoor fan, also called the condenser fan, is exposed to external conditions. As such it is most prone to dust and debris and the extreme weather. In desert climates, the outdoor fan motor is subject to heat not only from normal operation but from the outside temperature as well. As it starts to fail, the fan may work fine in the cooler morning hours but stop by afternoon. This can shut down the entire system for hours. When they stop running completely, your air conditioner will no longer work. Running a faulty fan will lead to compressor failure, which is a very costly repair.
Whether you’re looking for air conditioning maintenance, air conditioner repair, or a new air conditioning system, Sears Home Services can help. We’re your best, most-trusted option for fast, quick, and easy local service, repair, and maintenance of your home air conditioning system. If your air conditioner isn’t cooling or your central air conditioner is leaking water, we’ll connect you to the best local AC repair service technicians in the business.We have local technicians in your neighborhood that are highly trained, licensed, vetted, and guaranteed to help fix all of your air conditioning needs.
From Day 1, Alberto walked us through the process, and present us with a variety of options based our budget for the project. His customer service is the best as he did not oversell any services and did not nudge us towards buying a unit that would stretch our budget. On installation day, HVAC Services sent out a crew of 6-7 guys, all of whom were very polite and kept their work areas clean, and installed the whole system the same day.
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.
Is there a such thing as a PQ-15 valve? No…but how do we know? And oh, by the way, there are only two types of line-sets: 3/4 inch, and 7/8 inch. All modern equipment runs on a 7/8 inch line-set, so the only time they’ll have to change something is if you have antiquated 3/4 inch line-set from the 60’s or 70’s. I’m digressing though…the point is that they can easily prey on uninformed consumers…like you, baby bird! Don’t worry though…you’ll be flying by the end of this article.

Duct system installation and repairs affect HVAC installation cost. If you’re installing a new forced air heating or cooling system, your home must have ductwork – if you don’t have ducts installed, a new duct system will need to be designed and installed. Your existing duct system may require air sealing to eliminate air loss, helping your new heating and cooling system operate efficiently.
Pro HVAC company Southern Comfort Mechanical says on its blog, “If there’s mold growth inside the handler due to excess moisture, algae in the condenser drain line or a dirty evaporator coil, it can negatively impact your AC unit’s efficiency. The filters inside may also build up excess dirt and become clogged, which will also make your AC [or heat pump] waste energy trying to sustain the cool climate inside your home.” These issues are easy to solve. They don’t require replacing the air handler.
HVAC equipment is estimated to last about 15 to 20 years. Yet over the years, parts go out and need to be repaired. Heat sensors, exchangers, and ducts can become worn out. Air conditioning motors may need repairing from time to time. For repairs to your heating and air conditioning systems, and even general maintenance, let HomeAdvisor help. Enter your zip code and let us connect you with prescreened HVAC repair services near you.
×