The AC contactor (relay) and start/run capacitor(s) (see illustration below) fail most often and are inexpensive. So it's a safe bet to buy and install those parts right away, especially if your air conditioning service unit is older than five years. The condenser fan motor can also fail, but it runs about $150 — hold off buying that unless you're sure that's the culprit.
DIY: Most DIY installations go smoothly. The major brands have compatibility checkers to see which of their models will work with the wiring your old thermostat is using. Potential problems involve the need for a C-wire, or common wire, when the existing bundle doesn’t include one. There are solutions discussed in our Thermostat Buying Guide, linked to below.
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.
PickHVAC Tips: First, see the PickHVAC tip above about sizing a central air conditioner. It applies to heat pumps just as much. Secondly, Even if the line set for the new heat pump is the correct size, we recommend replacing the set or at least the fittings. Old lines and fittings are a major source of leaks. When refrigerant leaks out, the heat pump efficiency suffers. Eventually, the unit stops providing heating and air conditioning, and it might break down.

If the condenser coils are clogged, the compressor can overheat and shut down. You'll experience intermittent periods of minimal cooling, followed by no cooling. Even if you're “sure” the condenser coils are clean, clean them again. Turn off the power. Flip the air conditioning service and furnace circuit breakers in your main electrical panel to the “Off” position. Next, turn off the power switch right at the furnace or air handler. Then yank the disconnect block (Photo 1) and clean the condenser coils (Photo 2). If the air conditioning service still doesn't work properly after you've cleaned the condenser coils, installed a new filter and opened all the supply vents, proceed with the following repairs. Your AC won't work fully unless you do this.


The number of years an HVAC system lasts depend on the type and brand of components that make up your system. The lifespan of an air conditioner averages between 15 and 20 years. The life expectancy of a tankless water heater is approximately 20 years, while a storage water heater is closer to 10-15 years. Ducts may need replacing within 10-15 years. Your equipment will have a longer life if you have regular tuneups and maintenance to keep everything in good working order. If you’re having repair problems and your HVAC system is over 10 years old, it’s a good time to consider the costs and benefits of repairing vs. replacing. Energystar.gov provides the following tips to help you decide whether to repair or replace:
Air conditioner size is measured in “tons.” However, the tonnage of an HVAC unit is not actually based on its weight. A “ton” is simply a measure of an air conditioner’s ability to cool your home. One ton is the ability of your air conditioning system to cool 12,000 BTUs (BTU stands for British Thermal Unit) in an hour. Likewise, a “2-ton” central air conditioner is able to cool 24,000 BTUs per hour.
There is much more to air conditioning than AC installation in Fort Smith, AR then just maintenance and repairs. A variety of other services is required throughout the lifespan of your cooling unit. We are the professional team capable of completing them all. Replacements, troubleshooting, indoor air management, these are all part of our repertoire.
An example of a geothermal heat pump that uses a body of water as the heat sink, is the system used by the Trump International Hotel and Tower in Chicago, Illinois. This building is situated on the Chicago River, and uses cold river water by pumping it into a recirculating cooling system, where heat exchangers transfer heat from the building into the water, and then the now-warmed water is pumped back into the Chicago River.[24]

Before we get to HVAC installation prices, we will first need to briefly discuss some terms, definitions, and factors that will affect how an honest HVAC installation company determines their prices. Notice that I said honest. Unfortunately, there are dishonest people out there. There always have been, there always will be, and there is a good chance that you had an experience with such a contractor, which is what drove you to read this article. I can’t teach you how to tell if someone is honest, but I can give you the knowledge to help you decide. Take a look at How to Choose an HVAC Contractor for tips on what to look for.
No matter where you bought your air conditioning system, we can repair it. We have years of experience working with all the best central air conditioner brands such as Kenmore, Carrier. Trane, Goodman, and Rheem. As a result, you can rest assured we’re familiar with your air conditioning system and we have the parts you need to complete a successful air conditioner repair.
The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.
Although most new homes have ducts and vents already in place, many older homes have old convection heating systems or baseboard heaters without ductwork. In such cases, you will need to install ducts and vents to provide the air conditioning with a flow system. This would be the time to explore upgrading the existing heating system as well, as it will be much cheaper to do together.

Replacing a capacitor is easy. Just take a photo of the wires before disconnecting anything (you may need a reference later on). Then discharge the stored energy in the old capacitor (Photo 4). Use needle-nose pliers to pluck one wire at a time from the old capacitor and snap it onto the corresponding tab of the new capacitor. The female crimp connectors should snap tightly onto the capacitor tabs. Wiggle each connector to see if it's tight. If it's not, remove the connector and bend the rounded edges of it so it makes a tighter fit on the tab. When you've swapped all the wires, secure the new capacitor (Photo 5).


You've probably noticed many appliances boasting an Energy Star Certification. What this means is that manufacturer voluntarily built the product to help reduce greenhouse gases and meet non-regulatory guidelines offered by the Environmental Protection Agency. To earn an Energy Star rating, a product or system must be tested by a third party that has been recognized by the EPA for meeting their testing qualifications.
Lennox, on the other hand, is probably the most expensive unit out there and I can’t stand them.  In our (humble?) experience, they have a horrible logistics chain, making repair parts difficult to come by (sometimes taking weeks), poor customer service, and the parts cost three times as much. That’s not what this article is about, so read more in: Carrier vs. Lennox Furnace Review.
A little simple math can help determine the size system you need. A rule of thumb is 20 BTUs per square foot. So, a 500 square foot room would need 10,000 BTUs to cool or warm it efficiently. This assumes that you live in a temperate region and have adequate insulation with no energy loss. In the real world, all units have some degree of energy loss. This is reflected in an HVAC system's SEER rating for cooling and AFUE rating for heating.
Multiple inventions within this time frame preceded the beginnings of first comfort air conditioning system, which was designed in 1902 by Alfred Wolff (Cooper, 2003) for the New York Stock Exchange, while Willis Carrier equipped the Sacketts-Wilhems Printing Company with the process AC unit the same year. Coyne College was the first school to offer HVAC training in 1899.[12]
If the condenser coils are clogged, the compressor can overheat and shut down. You'll experience intermittent periods of minimal cooling, followed by no cooling. Even if you're “sure” the condenser coils are clean, clean them again. Turn off the power. Flip the air conditioning service and furnace circuit breakers in your main electrical panel to the “Off” position. Next, turn off the power switch right at the furnace or air handler. Then yank the disconnect block (Photo 1) and clean the condenser coils (Photo 2). If the air conditioning service still doesn't work properly after you've cleaned the condenser coils, installed a new filter and opened all the supply vents, proceed with the following repairs. Your AC won't work fully unless you do this.
Installing a split system may involve making modifications to the house itself for the necessary lines to be run. The heat exchangers are also more prone to picking up debris and must be cleaned on a regular basis. While they come with protective screens over the fan, care must still be taken to ensure that nothing gets in, especially in a home with children.
You can adjust for seasons: During the summer, you can have the air conditioner stay off during the cooler morning hours and start cooling the house as everyone gets up and starts moving around. During the winter, you can have your heater stay off while you are away at work and turn on about a half hour or so before you get home so that you are coming home to a nice, warm house.
We bought 2 top of the line Lennox HAC for $29,000 less about $3,500 rebates, thinking they would at least last 10 years. Well, after 6 years, the system leaked. We are paying $1,700 to fix that leak. We thought at least it is still under warranty - yes BUT - the warranty covered $15 & the rest we were up for ,even though they advertise 10 year warranty. We are trying to sell & move out of high cost southern Calif & have looked at 20+ places in Arizona. Most of the houses we looked at were built from 1998 to 2005. We asked if the HAC was original & in most case it was - even though the highs were 115 to 120 & the lows 90F - versus where we live the highs run 85 to 95 & the lows are in the 60s. I asked the repairman WHY ours went out at 6 years. He replied that they just do not build them the same anymore. In Arizona, I did not see any Lennox - mostly Trane or Carrier. We had Fujistu in Australia which were fantastic - nothing went wrong in the 9 years we had them. Also, they had full induction motors not like the energy consuming 2 stage motors in Lennox. Maybe the Japanese built Fujusita still builds quality & the warranty is meaningful?
They are also often harder to install. A proper location on the roof must be selected that can support the weight of the unit. Then a platform must be built and a drain pipe for the unit must be run along the roof to avoid problems with mold and corrosion. A crane must be used to lift the unit onto the roof while a team guides it into place and hooks it up.
Monday the following week, no phone calls, or follow up.  I call to get an update and am told that they cannot install my system because they don't have time.  I ask what does that mean, one year? One week? Until the end of summer they say.  What does that mean I ask?  They say at the end of September.  I say thank you for wasting 1 month of my time.
Indoor Coil -- The indoor coil is a heat transfer device. It absorbs the heat from the inside of the house and passes it on to the refrigerant and is pumped outside. Dust that builds up on the coil can hamper its ability to absorb heat. High heat transference coils use very thin metal. Airborne chemicals can cause corrosion which leads to leaks. The constant vibration of the compressor can also cause solder joints to weaken and leak. An indoor coil may operate for weeks with a tiny leak, and you may not notice the loss in performance right away. As soon as a leak is made known, it should be replaced or repaired immediately.
PickHVAC Tips: Installing the right size central air conditioner is extremely important. Have a load calculation done to ensure proper sizing. ACs that are too big aren’t as energy-efficient as they should be, and they cycle on and off too much. This creates over-cooling and temperature imbalance. Units that are too small run constantly in very hot weather and can’t keep your home cool. When an air conditioner is properly sized, it runs at optimal efficiency and indoor comfort.
AC air handler buzzing sounds. Do you hear a buzzing sound when you turn on the thermostat? The only thing that comes on in the house when you turn on the thermostat is the fan relay and fan in the air handler or furnace. Try switching the thermostat HEAT/COOL switch to OFF. Then switch the fan switch from AUTO to ON. The fan (only) should come on. If the air handler makes a buzzing sound, it probably has a bad fan relay or, more likely, blower fan.
×